contact
support
Download
order
news
AGG Software Forums
November 09, 2024, 07:44:18 PM
Welcome,
Guest
. Please
login
or
register
.
Did you miss your
activation email?
1 Hour
1 Day
1 Week
1 Month
Forever
Login with username, password and session length
News
: Welcome on our forum!
Home
Help
Search
Login
Register
AGG Software Forums
>
Online Help Center
>
Data loggers and plug-ins
>
Advanced OPC data logger - Siemens s7-1200
Pages: [
1
]
« previous
next »
Print
Author
Topic: Advanced OPC data logger - Siemens s7-1200 (Read 49334 times)
natisie
Jr. Member
Karma: +0/-0
Posts: 7
Advanced OPC data logger - Siemens s7-1200
«
on:
September 08, 2017, 02:00:00 PM »
I am trying to read OPC variables from a S7-1200 PLC. The problem is that these do not appear in the variables listed by the OPC data logger when connected to the simatic OPC server. The variable appear as:
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL*
But the variables that I should read are:
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL0
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL2
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL4
...
Siemens suggested me to look at the variables with the Matrikon Explorer that allows to change the names of the variables, I did and it worked.
I tried to do the same with the OPC data logger but I got the problem showed in the attached picture. I use the manual mode to define the variables with the corresponding number at the end as described above. However, I cannot longer use the Advanced OPC data logger due to this problem. I think I have to re-install it, but:
Any idea how I can define this variables in the Advanced OPC data logger???
datalogger error.JPG
(96.98 KB, 1086x515 - viewed 12 times.)
Logged
Arthur Grasin
Tech. Support
Administrator
Hero Member
Karma: +0/-0
Posts: 806
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #1 on:
September 20, 2017, 02:00:00 PM »
Could you send us the error report? We'll try to solve this problem.
Logged
natisie
Jr. Member
Karma: +0/-0
Posts: 7
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #2 on:
October 13, 2017, 02:00:00 PM »
Hi,
Here is the program protocol file. This is after I re-installed the software and trying again to configure manually the variables I need to read.
I couldn't find the error report.
Hope this is useful!
Thank you!!
opclogger.log
(33.87 KB - downloaded 3 times.)
Logged
Arthur Grasin
Tech. Support
Administrator
Hero Member
Karma: +0/-0
Posts: 806
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #3 on:
October 26, 2017, 02:00:00 PM »
Unfortunately, this log file is useless. Is it 100% repeatable? If yes, then please, provide a step-by-step instructions.
Logged
natisie
Jr. Member
Karma: +0/-0
Posts: 7
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #4 on:
January 19, 2012, 03:22:12 PM »
Hi Arthur,
My question is more focused on whether I can actually read the variables I am interested in by adding these manually. This is, instead of adding the auto detected variable:
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL*
Change this manually into:
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL0
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL4
OPC.SimaticNET.TCSB.1\TCS:[new project 1.1.101]DB1,REAL8
Is this possible with the Advanced OPC data logger? Do I need to do any special configuration?
Logged
natisie
Jr. Member
Karma: +0/-0
Posts: 7
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #5 on:
January 19, 2012, 03:42:27 PM »
Arthur,
I just got a email with an updated version of the opcsrc.dll file which I located into the correspondent program folder.
I still cannot do what I need
Logged
Arthur Grasin
Tech. Support
Administrator
Hero Member
Karma: +0/-0
Posts: 806
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #6 on:
January 19, 2012, 03:48:11 PM »
I've send a link to an update via email. The problem with manually added tags has been fixed.
Logged
natisie
Jr. Member
Karma: +0/-0
Posts: 7
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #7 on:
November 11, 2017, 02:00:00 PM »
I have updated the latest opcsrc.dll file I got via email, but I still cannot add a manual variable. It says that doesn't exist.
Do I need to do something else?
Logged
Arthur Grasin
Tech. Support
Administrator
Hero Member
Karma: +0/-0
Posts: 806
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #8 on:
November 11, 2017, 02:00:00 PM »
Please, remove all groups and items from the program configurations and add it again from scratch.
Logged
natisie
Jr. Member
Karma: +0/-0
Posts: 7
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #9 on:
November 20, 2017, 02:00:00 PM »
Arthur,
I have done the following:
- updated the opcsrc.dll file
- deleted all the groups and variables
- restart the PC
- created again the OPC configuration
- added a manually and a auto detected variables
I got:
19/01/12 14:03:22 OPC interface. Error while initializing the OPC server "OPC.SimaticNET.TCSB.1 (TCS:[new project 1.1.101]PLCConnected) - Access violation at address 0591474E in module 'opcsrc.dll'. Read of address 00000000"
19/01/12 14:06:30 OPC interface. Variable "OPC.SimaticNET.TCSB.1 (TCS:[new project 1.1.101]DB1,REAL0)" doesn't exist!
19/01/12 14:06:40 OPC interface. Error while initializing the OPC server ": Server ProgID must be specified"
19/01/12 14:06:51 OPC interface. Error while initializing the OPC server ": Server ProgID must be specified"
Logged
Arthur Grasin
Tech. Support
Administrator
Hero Member
Karma: +0/-0
Posts: 806
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #10 on:
January 19, 2012, 07:39:52 PM »
Please, create a backup of your configuration (from the File menu) and attach it here. I'll verify it.
Logged
natisie
Jr. Member
Karma: +0/-0
Posts: 7
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #11 on:
December 08, 2017, 02:00:00 PM »
I have attached the backup
OPCtest.ini
(4.01 KB - downloaded 2 times.)
Logged
Arthur Grasin
Tech. Support
Administrator
Hero Member
Karma: +0/-0
Posts: 806
Re: Advanced OPC data logger - Siemens s7-1200
«
Reply #12 on:
December 19, 2017, 02:00:00 PM »
I see only one OPC tag in this configuration that has been added automatically and therefore the tag name contains "*" at the end of the name.
Logged
Pages: [
1
]
Print
« previous
next »
Jump to:
Please select a destination:
-----------------------------
News & Feedbacks
-----------------------------
=> News and Updates
=> Site Comments
-----------------------------
Online Help Center
-----------------------------
=> Advanced Serial Port Monitor
=> Data loggers and plug-ins
=> Data loggers ActiveX
=> Advanced USB Port Monitor
=> Virtual Null Modem
=> Software for DNC and CNC
=> Other questions
-----------------------------
Development
-----------------------------
=> Feature Requests
Loading...