The16 bit integer values from the modbus register are already working fine and I do this for the very first time. My only remaining problem I have to solve:
I am pulling in 32bit Floating Point data from various Registers, which are not parsed my the modbus tcp plugin correctly. What we Need to Export into Excel is a normal decimal integer.
Do I have to use the expression module or is there another source of error? ::)
Thanks for your Input!
Does the program display float values correctly in the DDE server plugin (active items)?
No, there is no floating point number in the active items.
I always get the default value.
Please, attach a screenshot with your parser items from your MODBUS queue.
Here is the setup, please see the screenshot attached.
The 32 bit float holds 2 registers (each register contains 16 bit). Please, specify to read 2 registers in your queue.
You made my day Arthur! ;D Thanks!